Found the formula for lag bolt allowable withdrawal load. "Marks Standard Handbook for Mechanical Engineers" Won't say how long ago I bought that book for school. Can't be that long ago its only the 8th edition.
Sorry don't remember how to write formula on the computer but here it is.

P=1800D(to the power of 3/4) G ( to the power of 3/2)

Where D = shank dia of lag
G = specific gravity of wood

Most construction material is SPF spruce pine or fir.
The lowest being pine at .43
So for a 3/8 lag in pine side grain you get 243 Pounds pull out strength per inch of thread.
Think I went 2 1/2 lags to get 2 in of thread into the joists or 486 pounds per lag at 2 per joist 972 pounds on each joist. Spread the load over 3 joist gives 2916. Derate by a factor of safety of 3 and you get close to 1000 pounds if the load is at the wall, worst case scenario.
My ceiling was sheeted with chip board which I wasn't about to remove.
Not sure the 1/2 inch bolts your thinking of using would give much more strength with 2 inches of wood for pullout on the joists. Don't know where you'd get the numbers for that.
Just food for thought.